My company plans to adopt not needed space (around 20 square meters)in to a laboratory where some OSD form will be tested (something like microlaboratory).
I'm asking does somebody knows any HVAC requirements for this type of rooms ????
 
General micro lab can be of C grade, however refer to local pharmacoepiea. Sterility testing should be of class B with a two/three change room concept. You need to maintain atleast 40ACPH in micro and 60ACPH in sterility testing lab. Labs should be at positive pressure w.r.to change rooms. Actual testing in both cases should be under LAF.

 