chankawai

Geotechnical
Feb 8, 2007
2
I need to find a way (in the lab) to test the resistivity for aggregate having a nominal size of 3/4" with very little fines. The material will not conform to AASHTO T 288. Does anybody know of a way to do this?
 
Replies continue below

Recommended for you

Resistivity to electric current or to sulfides and salt attack?
 
Need to go to the stockpile or pit where this material is from to get probes at a respectable distance apart. (lab dimensions will be too rough, =/- 50%).
 
That spec is for minimum resistivity in the lab. It's used as a lower bound for resistivity. The idea being a soil with lower resistivity has a higher corrosion potential. If you're working with aggregate, the resistivity is likely to be very high. Because of this, aggregate itself usually wouldn't be that corrosive. The only case that I think it could be is if the aggregate is saturated in the field and the pore water has a high concentration of soluable salts.
 
Resistivity is a necessary parameter in the design of grounding for electrical substations. Low resistivity gives a safe ground system with larger grid of buried copper conductors and maybe no need for drilling a well for grounding purposes.
 
I wouldn't count on open graded, unsaturated aggregate having good enough properties to place a ground mat within it. In fact, this material is typically used to eliminate step potential when it is a concern.
 