Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

kitchen grease duct through a loading dock.

Status
Not open for further replies.

rmusa

Mechanical
Joined
May 29, 2016
Messages
23
Location
US
We have a 4500 cfm grease exhaust duct tied to a hood. The duct will penetrate wall behind kitchen and then go through a two bay loading dock and then to the exterior. The walls around the loading dock are 3 hr rated.

The duct will have standard 2 hour rating, double wall manufactured with insulation. Fire dampers are not allowed in the duct. How can this duct be installed in the loading dock?
Does the rating of the duct need to be increased to 3 hour? Will 2 hour duct work?
Can we build a 1 hour enclosure around the duct. Is 2 + 1 hour additive?
 
Not additive in this case. Build 3 hour chase around the duct to separate the duct from the room. Delta $ between 1 hr and 3 hr. chase would justify the labeling requirements or future questions.
 
If this is a horizontal grease duct, make sure drain pans and cleanout doors are accessible.
B.E.

You are judged not by what you know, but by what you can do.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top