Kitchen Exhaust fan duct sizing

Status
Not open for further replies.

marthab

Civil/Environmental
Nov 19, 2002
24
How do I size the duct for an exhaust fan with 1450 cfm and 1,324 rpm.
 
Replies continue below

Recommended for you

Fans have a performance curve that defines cfm vs. external pressure drop.

Step 1: Find this curve for your fan.

Step 2: Decide how many cfm you need, and use the curve to identify the corresponding allowed external pressure drop.

Step 3: Size the duct for that pressure drop at the required cfm.
 
marthab,

This isn't an exhaust hood over a cooking appliance, is it? If so, you'll have to also consider keeping the velocity of the air high enough to entrain the particulates and grease. If not a kitchen application, listen to MintJulep.

Good on ya,

Goober Dave
 
Marthab
I do not know where you live, but here is a PDF of the code guidelines where I live. Most states are not that much different.
Pay attention to page 10.

B.E.


The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor
 
Find and employ a Mechanical engineer and don't try to bootstrap this.
 
Berkshire
I am surprised that NFPA 96 is not part of the listed standards governing the design and installation of kitchen exhaust systems in your neck of the wood.

Also: NFPA 96 allows lower velocities as low as 500 FPM nowadays for some specific applications such as Melink control systems.
 
It is and the guidelines mention it.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor
 