just getting started

Status
Not open for further replies.

Guest
I am interested in getting started in the circuit breaker testing and maintenance field. I would like to do this right, and am looking for some guidance in finding the training and certification programs that are required, and informative. I would also appreciate some information on the equipment that I will need. I have been to the Megger web-sight and am considering perchasing a Multi-Amp model DDA-3000, any sugestions? Any information would be greatly appreciated.

Thanks,
 
Replies continue below

Recommended for you

I suggest to contact testing companies or manufacturers of circuit breakers. Some of then could be in the US:

Testing Companies
a- Doble Engineering

Breakers Manufacturers:
b- ABB Circuit Breaker Plant- Greensburght, PA.
c- Alstom Circuit Breaker Plant- Pittsburg, PA.
d- Siemens Circuit Breaker Plant
e- GE/Hitachi.
 
Thanks for the help cuky2000 & jbartos. If you have any questions about infrared applications feel free to drop me a line at irthermalimage@cs.com.
Thanks again,
 

Learn about the effects of reactance in circuit-breaker injection testing.
 
check out schneider group ...Merlin Gerin in particular