CanuckEngineer
Electrical
- Feb 9, 2009
- 45
Hey guys,
Great forum here.
I am usually on the electrical side but I recently was posed with some issues on the Operations side of one of our buildings.
Please feel free to read the sequence below and provide any comments. I am working on gathering supplemental data like BAS shops and mechanical schematics to help out.
Thanks,
RK.
Stage 1: If EF-1 or EF-5 or EF-8 runs, then EF-20 runs at 40% to match the capacity of 1 fan.
Stage 2: If EF-1 & EF-5 or EF-1 & EF-8 or EF-5 & EF-8 run, then EF-20 runs at 70% to match the capacity of 2 fans.
Here is where we start having problem.
When EF-20 switch from stage 1 of 40% to stage 2 of 70%, the amp draw would jump up to 42 amp and stay there. However, if we was to have EF-20 goes to 0% then ramp up to 70%, it would run just fine and not overload at all, and the amp draw was only 20 amp.
What we also noticed was that when the fan switch from 40% to 70% without the full shutdown reset the amp draw would jump up to 42 amp then stay at 42 amp at 70%, 80%, 90%, & 100%.
Stage 3: If EF-1, EF-5 & EF-8 all run, then EF-20 runs at 95% to match the capacity of 3 fans. We found only 2 ways to get EF-20 to 95%.
By having a full shutdown reset and then bring the fan from 0% to 70% then 95%. The idea here is to get the fan to stage 2 first then to Stage 3.
By having a full shutdown reset then bring the fan from 0% to 95%.
The amp draw at 95% is 30 amp or so using the 2 methods above. Without the full shutdown reset between the stage the fan would just go to 42 amp and stay there when ramping up from 60-100%.
We also notice that the ramping up time had no effect. As we had tried to have the fan ramping up really slow and this 42 amp jump still happened.
If anyone else had any other comment or observation please feel free to add in.
Great forum here.
I am usually on the electrical side but I recently was posed with some issues on the Operations side of one of our buildings.
Please feel free to read the sequence below and provide any comments. I am working on gathering supplemental data like BAS shops and mechanical schematics to help out.
Thanks,
RK.
Stage 1: If EF-1 or EF-5 or EF-8 runs, then EF-20 runs at 40% to match the capacity of 1 fan.
Stage 2: If EF-1 & EF-5 or EF-1 & EF-8 or EF-5 & EF-8 run, then EF-20 runs at 70% to match the capacity of 2 fans.
Here is where we start having problem.
When EF-20 switch from stage 1 of 40% to stage 2 of 70%, the amp draw would jump up to 42 amp and stay there. However, if we was to have EF-20 goes to 0% then ramp up to 70%, it would run just fine and not overload at all, and the amp draw was only 20 amp.
What we also noticed was that when the fan switch from 40% to 70% without the full shutdown reset the amp draw would jump up to 42 amp then stay at 42 amp at 70%, 80%, 90%, & 100%.
Stage 3: If EF-1, EF-5 & EF-8 all run, then EF-20 runs at 95% to match the capacity of 3 fans. We found only 2 ways to get EF-20 to 95%.
By having a full shutdown reset and then bring the fan from 0% to 70% then 95%. The idea here is to get the fan to stage 2 first then to Stage 3.
By having a full shutdown reset then bring the fan from 0% to 95%.
The amp draw at 95% is 30 amp or so using the 2 methods above. Without the full shutdown reset between the stage the fan would just go to 42 amp and stay there when ramping up from 60-100%.
We also notice that the ramping up time had no effect. As we had tried to have the fan ramping up really slow and this 42 amp jump still happened.
If anyone else had any other comment or observation please feel free to add in.