I'm not sure why a fire pump is being mentioned. A pressure maintenance pump (a.k.a., jockey pump) is only required for a NFPA 20 fire pump installation. It has no relevance to a dry pipe valve. The original poster asked a question and used components that don't have a relation to each other.
All dry pipe valves (DPVs) require either an air or nitrogen source to maintain the minimum required differential pipe so the valve's seat is maintained in the closed position. This pressure is based on the static pressure of the water supply. Below the valve seat, the pipe is filled with water; above the DP valve seat or diaphragm, the pipe is dry. Activation of a sprinkler begins to exhaust the air or nitrogen, which reduces the pressure below the required differential pressure and as a result, the DPV is opened, water fills the sprinkler pipe and discharges through the open orifice.