there is a difference between just building material, and the building component, be careful. for a window for example you have the glass U-value, but that doesn't take into account the frame. So you need the overall U-value. For a stud wall you need to take into account the studs (metal, wood) and the insulation in between. Our code has some calculation procedure how to account for that. Surprisingly your R-19 insulation maybe gives you an R-11 wall, or so. If you have bricks, there is a brick and the mortar joint. with highly-insulating bricks that can make a huge difference to have those thermal bridges.
now I don't know what manual J gives you, that is fr residential calculations. There should be an explanation in the manual. Maybe manually calculate the R-value of a composite wall, and compare it to Manual J? then you know how they did it. Possible Manual J gives some slack for other thermal bridges, in corners, around openings etc.
As said before, air infiltration can be the dominant heat load anyway.