Assuming you are following NEC (please verify):
The term "isolated ground" is misleading, and does not appear in the NEC. The applicable paragraph is NEC 250.142(D), Isolated Receptacles.
As mentioned above, this paragraph permits a receptacle to have the ground terminal insulated from the yoke, a separate insulated conductor is run from the receptacle back to a ground bus in the source panel or upstream panel. It is not truely "isolated", the resistance between the grounding terminal and yoke is very low once the required insulated grounding conductor has been installed. Such receptacles are identifed by their orange color or by a small orange triangle on their face (I don't believe the orange color is an NEC requirement, I think it's UL).
NEC, in general, requires all grounding systems to be bonded together in at least one point. NEC requires that the neutral and ground be bonded in one point (or sometimes two).
Be aware that overcurrent protection in the neutral is typically prohibited by 240.22 unless it simultaneously opens all phase conductors. Also, as mentioned above, an overcurrent device in the neutral would typically serve no purpose, with two specific exceptions:
1. It can facilitate maintenance if there are high neutral voltages present.
2. It is required if you are using the OC device to switch between two separately-derived 4-wire systems. This is rare, and can be more technically challenging than it first appears, and I'd generally recommend dual 3-wire (vs. 4-wire) systems with downstream transformers if you do have a legitimate reason to require transfer between separately derived systems.
Hope this helps.