PMS:
Consider a distributed generation system.
One set is the swing set and is using the Integral function of the governor. (Not all governors will have this feature, most are simple Proportional (Droop) control)
As the system load increases, the swing set will pick up the added load.
When the load on the swing set reaches a predetermined limit, the PMS will add generation to the system.
This may be directing a hydro unit to go from 10% output to 90% output.
The PMS will continue to add generating capacity until the load on the swing set drops into a predetermined range.
When the load on the system is decreasing, the swing set load will be dropping and the PMS will remove capacity until the swing set loading rises into a predetermined range.
This is automatic in most utilities as far as I know.
At one time it was manual.
Operators in a load dispatch center would monitor the load on the swing set and would direct the operators at individual generating sites to add or remove capacity.
This was originally done over a POTS. (Plain Old Telephone System)
Years ago I was visiting a very old hydro station. It was completely manual.
While I was there, the telephone rang. It was the load control center instructing the operator to take one set from 10% to 90%.
The operator turned a switch that activated a solenoid valve and directed water to a small pelton wheel driving a hydraulic pump.
He then moved over to another control that activated a solenoid valve on the hydraulic system.
Down on the floor, a very tall hydraulic cylinder started to extend. It was connected to a bell crank that controlled the water gates.
While doing this he was watching his power factor meter.
As the set was loading up, the PF was dropping.
He moved over to another control that increased the excitation and raised to power factor.
When I said manual, I meant completely manual. these sets did not even have Automatic Voltage Regulators.
The operator adjusted the excitation several time before the set was up to 90% output.
Note: At 100% load, the set may not have reserve to help support block loading.



I believe that the commutator machine is an exciter. The output would be controlled by rheostat control of the exciter field.