What if you had no swing set- just "sped" or "slowed all 10 gens to match the load as it changed?
Droop control is a basic feature of a diesel governor.
With all parallel sets at the same droop setting the sets will share the load in proportion to their capacity.
Droop control nicely limits the over speed and allows service to continue at no more than a 5% increase of frequency in the event that the swing set drops offline.
Other feature such as integral or reset will be added on top of droop control.
For example for the swing set. The first response to a load change will be a droop response.
This will cause a deviation from 60 Hz.
The integral or reset function will detect the error from the 60 Hz set point and bias the set point to bring the frequency back to 60 Hz.
On a large system the load typically does not change that fast.
When a load change is considered as a percentage of the total load and over the time constant of the integral function, the actual frequency deviations are generally much less than the 5% droop.
In the event that a generator was fully loaded, and lost all of the external load and the swing set connection, the frequency of the station service transformer would rise to 63 Hz.
This is a very worst case and is still acceptable.
Our very small plant, total 2.2 MW, had five diesels. They ran in droop with no swing set.
While the governors responded to load changes by following the droop curve, the operators manually trimmed the governor set points to keep the frequency at 60 Hz. It was rare that the frequency would be off by more than 1% or 2%.
Block loading.
We had two out-going circuits.
Our system could not take block loading of a complete circuit.
Our system went online by manually closing in each circuit one phase at a time.
This was a special case.
A larger system would be expected to have enough outgoing circuits that circuits could be switched in sequentially so that the block loading was within the capability of the generator(s).
Most systems of this size or smaller will be privately owned and the load will be under the control of the owners.
Consider an industrial plant on a self owned, islanded set.
Typically, after an outage, the large motors will be offline and will be restarted sequentially.
Our worst block loading was residential circuits.
As well as the transformer inrush, almost all of the refrigerators, freezers and A/C units would be drawing starting surges.
Extra reading.
PID controllers.
Droop control is the P of PID.
The swing set uses the PI of PID.
When you get your head around basic Proportional control the addition of integral will come easier.
A hint: Set loading. Consider a set in parallel with an infinite grid. The grid controls the frequency.
With 5% droop and the governor controlling at 60 Hz, the set will be unloaded.
As the control point is advanced, the set tries harder to raise the infinite grid frequency by opening the throttle and picking up more load.
When the governor is controlling at 105% or 63 Hz, the throttle will be 100% open and the set will be at full load but the frequency will be at the frequency of the infinite grid.
The error correction of the swing set helps the grid to appear infinite. (After the short correction period.)
To put a set online, the frequency is slightly above the grid frequency (In the order of 60.1 Hz to 60.15 Hz.)and the set synchronized and closed in.
The set will be supporting just enough load to prevent a reverse current trip.
The governor setting is then increased until the set picks up the required load.
Bill
--------------------