FreddyNurk asked:
I'd be interested to know the largest islanded systems in existence.
Hmmm...when does an island become a continent?
I'm not trying to be funny; some islanded systems become so large their operation, behaviour and characteristics are little different than that of interconnections.
Mbrooke asked:
What are the black start procedures? I'm really curious how you would control a radial load at the generating station. It would be amazing to see adjusting all the excitation result in a .5% increase of real load.
In my province, black start procedures are not carved in stone; we are instead provided with a series of black start guidelines [ which can be found in the Ontario Power System Restoration Plan, a public version of which is available at
] that we employ in choosing the best way to rebuild a system or portions thereof, since true system collapses, whether partial or almost complete, very rarely happen the same way twice.
Addition via Edit: The Electrical Reliability Council of Texas has a system fundamentals manual available at
where you click on the little pdf link to download the document; the System Restoration section begins on pg. 548, and states much the same thing as the OPSRP.
"Control a radial load at the generating station" - huh? If the scenario is one of a smallish electrical island with one control facility for generation, transmission and distribution, it is entirely possible to control a radial load
from the generating station using a SCADA system, but
at the generating station? Even peak shaving via voltage reduction is performed at < 50 kV, generally by providing a means of biasing the mid-point of the voltage regulation control band downward by three or five percent; the operation of the HV system remains unaffected. Indeed, when 3 or 5% voltage reduction is applied in my province due to system conditions, 3 or 5% V/R is indeed applied to the transformer secondary control bands, which lowers the 44 kV voltage to suit...but our residence remains unaffected, or at least is not affected for very long, since the under load tap changers at the 44 kV fed distribution station that supplies the local customers operates autonomously, and any reduction in 44 voltage that lowers the 8 kV distribution voltage is soon corrected by the ULTCs.
It is for this reason that lowering the voltage on all the generator terminals would be pointless.
Hope this helps.
CR