ASHRAE 90.1 now requires static pressure reset. Use of MVD's resulting into set airflow at all times to all branches will actually violate 90.1
About the article:
As a lesson learned - Always add a note in your general notes saying that "in case of conflict between drawings and specifications, the highest cost item shall apply." It removes the stupid notes left out in details that are never edited, such as in this
In the case study, I see ovewhelming evidence that the A/E was right. I bet that the outcome will be in favor of the government.
The case references "high velocity" and is defined per SMACNA 1975. SMACNA 75 is absolute, we no longer talk of high pressure, low pressure, etc, we talk about 2", 4", 6" etc. Matter of fact, ductwork for VAV systems upstream of VAV boxes is considered "Medium pressure", not high pressure, thus the note referring to HP in the article is actually not applicable at all.
And finally, just because someone wrote an article about a case study involving a litigation and got "published" in ASHRAE does not mean that this is the new ASHRAE guideline -References to ASHRAE should be pulled from the 4 books, not from articles written by its members.
In my opinion, installing MVD's upstream of VAV boxes is simply stupid, it is stupidely expensive and useless on everyone, it would be buying disease with your own money.