When I worked at a steel mill decades ago, we had an ungrounded 480V delta system. In the electric shop, they had 3 light bulbs connected to the main switchgear. If there was a ground fault anywhere in the mill, one lamp glowed brighter to let us know, but other than that, nothing shut down because that would have been a MAJOR catastrophe. That was the point of having an ungrounded delta system; the first ground fault was tolerated because it just made your system a corner grounded delta system and everything (other than where the fault was) continued on normally. I used to call it the "Damn the torpedoes, full steam ahead!" approach to plant operation.
So when that lamp glowed bright, we would get on the radio and ask who in the plant was having problems or seeing smoke, or if nobody responded we would jump in golf carts and drive around like keystone cops looking for it. Good times...