sberbece
Electrical
- Sep 15, 2003
- 39
Hi !
I am writing this tread to kindly request your opinions.
I came across a Client technical specification for low voltage induction motors that states:
“Motors shall be able to start under applicable load conditions with 75 % of rated voltage at motor terminals for DOL.”
I believe that this requirement exceeds the conservative approach and specifies a motor bigger that necessary, resulting an overall plant poorer PF and efficiency.
It also contradicts the AS/NZS 3000 clause 3.6.2, from which I can understand that the voltage droop at the motor terminals can not exceed -15 % (-10% power system variation & -5% voltage droop in cable) when supplied from a power system or 11 % when supplied from a standalone power system.
Therefore, a motor supplied by a power system which complies with AS standards shall never have to start when the voltage at its terminals is below 80% Un.
What do you think, specifying a minimum 80%Un at motor’s terminals is conservative enough? and
Is there a considerable difference regarding the motor size, its PF and efficiency, between a motor able to DOL when 80%Un and a motor that starts DOL when 75 %Un ?
Thank you in advance for your time.
I am writing this tread to kindly request your opinions.
I came across a Client technical specification for low voltage induction motors that states:
“Motors shall be able to start under applicable load conditions with 75 % of rated voltage at motor terminals for DOL.”
I believe that this requirement exceeds the conservative approach and specifies a motor bigger that necessary, resulting an overall plant poorer PF and efficiency.
It also contradicts the AS/NZS 3000 clause 3.6.2, from which I can understand that the voltage droop at the motor terminals can not exceed -15 % (-10% power system variation & -5% voltage droop in cable) when supplied from a power system or 11 % when supplied from a standalone power system.
Therefore, a motor supplied by a power system which complies with AS standards shall never have to start when the voltage at its terminals is below 80% Un.
What do you think, specifying a minimum 80%Un at motor’s terminals is conservative enough? and
Is there a considerable difference regarding the motor size, its PF and efficiency, between a motor able to DOL when 80%Un and a motor that starts DOL when 75 %Un ?
Thank you in advance for your time.