I was recently looking for a replacement off-the-shelf DOL motor starter for a wood jointer that is configured for 1ph 110v (definitely not industrial grade) and saw this listing for a 2HP rated 1ph 110v starter assembly:
The starter is using a Taian "Teco" CN/CU-16 contactor w/110v coil, and an O/L relay with a 22-30A dial range (as visible in the photos shown at this link to the manual):
Here is a link to the spec sheet for the Teco CN-CU/16 contactor:
Per the spec sheet the size 16 contactor is rated (for AC3 rated purposes) at a max of 13.5A under IEC 60947-4-1 spec and 20A under UL508 spec.
I emailed the company regarding the wisdom of selling a starter with a contactor that is rated at 16A continuous / 20A max with a 30A max thermal O/L relay. After several emails with no response from tech support or customer service, I emailed someone in management, who finally responded that they would look into it and get back to me.
Did I over react? Presuming you have 1 ph 110v 30A circuit breakers in place and need this starter, isn't this asking for eventual failure/contact welding/fire?
This is a good company, with a good reputation, and it was out of concern that I considered this when I contacted them.
Thanks in advance,
RC
The starter is using a Taian "Teco" CN/CU-16 contactor w/110v coil, and an O/L relay with a 22-30A dial range (as visible in the photos shown at this link to the manual):
Here is a link to the spec sheet for the Teco CN-CU/16 contactor:
Per the spec sheet the size 16 contactor is rated (for AC3 rated purposes) at a max of 13.5A under IEC 60947-4-1 spec and 20A under UL508 spec.
I emailed the company regarding the wisdom of selling a starter with a contactor that is rated at 16A continuous / 20A max with a 30A max thermal O/L relay. After several emails with no response from tech support or customer service, I emailed someone in management, who finally responded that they would look into it and get back to me.
Did I over react? Presuming you have 1 ph 110v 30A circuit breakers in place and need this starter, isn't this asking for eventual failure/contact welding/fire?
This is a good company, with a good reputation, and it was out of concern that I considered this when I contacted them.
Thanks in advance,
RC