Is the Allowable 4' Horizontal Offset Deleted Now?

Status
Not open for further replies.

msquared48

Structural
Joined
Aug 7, 2007
Messages
14,745
Location
US
Another structural engineer recently told me that the allowable 4 foot offset for combining shear walls into one shearwall line (flexible diaphragm analysis only) has been deleted from the 2006 IBC / ASCE 7, and the new offset value is only 6 inches. Can anyone confirm or deny this with a code reference? I cannot find it. Thanks in advance.

 
I did finally find the IBC section - 2308.9.3 - apparently still allowing the 4 foot horizontal offset. I still wonder though if there is a code exception/restriction to this allowance somewhere else in the code.

 
It was a misinterpretation of ASCE 7, section 14.5.2. No worries.
 