Intentionally manipulated? Probably not.
But I think you are misinterpreting it.
No offense intended.
Suppose you suddenly put the same transducer in a fridge, and measured its output at 5 second intervals. I suspect you'd see a stairstepped curve, and the first step below 71.8 would be around 71.2. No matter how many digits it's reported to, the measurement resolution appears to be somewhere around 0.6, maybe 0.5. It just happens to have not been calibrated to change from one value to the next on a nice integral number.
We're nearing the limits of my expertise on instrumentation, and you need more help than anyone could give you here. You need to read up on this stuff, or get help in the same room with you.
Mike Halloran