Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Is it necessary to provide ECC (Earth Continuity Conductor) for Single Point/ Mid-Point Bonding? 1

Status
Not open for further replies.

Rejeckted

Electrical
Mar 7, 2021
37
Dear all,

The types of sheath bonding that are generally used for Cables is (a) Single Point (b) Both Point Bonding or (c) Cross-Bonding

But as we know that generally when using Single Point or Mid Point Bonding we provide with the SVL to limit the sheath voltage. What is the requirement of ECC and is it essential and must provide? Is there any alternative method of providing earthing or shall it always be under Manufacturers purview.

Thanks
Chris
 
Replies continue below

Recommended for you

IEEE 575/2014 IEEE Guide for Bonding Shields and Sheaths of Single-Conductor Power Cables Rated 5 kV through 500 kV
6.3.3 Parallel ground continuity conductor :
Accordingly, it is recommended that single-point bonded and multiple single-point bonded cable installations be provided with a parallel GCC that is grounded at both ends of the route as shown in Figure 2. The spacing of this conductor from the cable circuit should be sufficiently close to limit the voltage rise of the shield/sheath to an acceptable level during a single-phase fault. The size of this conductor must be adequate to carry the full, expected fault current for the cable system.
 
 https://files.engineering.com/getfile.aspx?folder=c02d1994-cac6-43ee-912d-94fb2a61e4f7&file=Single_point_grounding_and_EGCC_ieee_575.jpg
Thank You very much @7anoter4. So it is to stop from Sheath Voltage to Rise Beyond Limits sustainable by SVL (To dissipate the Energy during Fault)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor