Here is my Tank spec's:
between 40-60F, 630K Gal, 54x36', Above Ground, storage of thermally stratified chilled water based on 650T of Peak Cooling Load, 40F Chilled Water supply to 56F.
************************************************************
unclesyd (Materials) Jan 14, 2004
____________________________________________________________
We use asphalt impregnated felt(single layer) under some tanks, mainly heated as in you case. We have some large floating roof storage storage tanks also with felt. I would use it as it is a good thermal brake though some of the newer grouts are good insulators but a lot more trouble.
____________________________________________________________
What temperature are you going to operate the tank?
40-60F
What type foundation is your tank going to sit on?
We required concrete ringwall foundation meeting the requirements of AWWAD100, AWWA D-10387, and ACI 318. Contractor provide submittals for 4000psi concrete, 2.5ft depth, 2225 PSF Press at base.
____________________________________________________________
My question: Do you know thermal property of Impregnated-Asphalt Felt so I can compare between Grout & Asphalt Felt?
************************************************************
SteveBraune (Structural) Jan 14, 2004
If you are asking about CP of the interior, I'd say that it all depends on your water characteristics. We write plans and specs for water tanks for many uses and find that the answer is not obvious.
____________________________________________________________
My Question: What would considered a good lining system, can we test the interior lining? Can you explain the relationship between lining & cathodic protection?
************************************************************
Your helps are greatly appreciated and your knowledge will pass along to others. Thank you!