I did not get the answer I was looking for. I have legacy installations 40 plus years old and I am not ready to spend huge amount of money refrofitting EGC, 1000 plus circuits, if not required by law. In a HRG system, ground fault current for a single phase to ground fault is limited, 5A to 10A and does not trip the protective devices. The risk of shock hazards to workers can be managed by implementing operating discipline procedures which will require proper PPE for any worker coming in contact with the energized raceways. For a second line to ground fault, the fault current will be high enough to trip the overcurrent protective device. Please address my concerns.