Bill, your ampere-turn math doesn't seem to be correct with two turns of the primary through the window to create a 100/0.5 A CT out of a 100/1 CT. A 100/1 CT has 1 primary turn and 100 secondary turns. You'd need to have a 1/2 turn in the primary with 100 A to get 0.5 A on the secondary; needless to say, that can't be done.
I think using a 200/1 CT as edison123 originally suggested is correct - with 100 A in the primary, 0.5 A will flow in the secondary. There's no need to wrap any primary or secondary conductors through the window with a 200/1 CT.