I am doing a SDS D seismic upgrade to a 3 story shotgun type building that is on the historic registry. Given this I have very little ability to move interior walls so that they align with the walls below. This results in the transverse non-bearing walls being offset by 1' to 3' with very few ending on a bearing line below.
I am designing new transfer beams under each wall to receive the end of wall reaction / hold down and transfer them to the exterior wall or centerline girder. The Girders will then carry the vertical reactions to the posts to ground. Per ASCE 7-10 section 12.3.3.3 these framing members and their connections will need to resist the seismic load effects including overstrength factor of 12.4.3.
My understanding is that the shear wall elements themselves will be designed per the normal loads of 12.4.2 and the over-turning vertical reactions will need to be increased by Ω0 and equations 5 & 7 in 12.4.3.2. Does this sound correct?
At locations where the end of these walls are in the exterior wall over the foundation do the hold downs need to also be design with overstrength? My thinking is that the beams and connections need to be at overstrength but the posts and wall hold downs do not because they do not have a horizontal discontinuity.
I am designing new transfer beams under each wall to receive the end of wall reaction / hold down and transfer them to the exterior wall or centerline girder. The Girders will then carry the vertical reactions to the posts to ground. Per ASCE 7-10 section 12.3.3.3 these framing members and their connections will need to resist the seismic load effects including overstrength factor of 12.4.3.
My understanding is that the shear wall elements themselves will be designed per the normal loads of 12.4.2 and the over-turning vertical reactions will need to be increased by Ω0 and equations 5 & 7 in 12.4.3.2. Does this sound correct?
At locations where the end of these walls are in the exterior wall over the foundation do the hold downs need to also be design with overstrength? My thinking is that the beams and connections need to be at overstrength but the posts and wall hold downs do not because they do not have a horizontal discontinuity.