Congratulations abref, you solved the problem yourself.
But let me try to provide answers on the further questions.
Dead time is the time provided by the control unit to avoid short circuit within a phase leg. This time usually is choosen by the engineer designing the drive so that short circuits are avoided under worst case conditions.
The delay time of the drivers and the IGBTs have to be considered, distinguising between turn on and turn off. Usually ample safety margin is provided.
But if, for a given switching frequency, the dead time is set to high this will result in loosing headroom for modulation and, more severe, instable operation of induction motors under V/f control or nonlinearities in more sophisticated control schemes.