DrDrreeeaaa
Electrical
- Apr 25, 2008
- 266
Hi All
We have a Zone 1 IIA T3 (IEC) Hazardous area in which we are installing several intrinsically safe circuits
Were using Siemens ET200iSP which is an intrinsically safe IO rack system
Anyway, there's a line in the Siemens IO manual that says you're not allowed to connect the equipotential bonding system to the protective earthing conductor of the supply system.
It also says that the ET200isp rack and most of the Is equipment (including cable screens) needs to be connected to this equipotential earthing system.
I understand that they are trying to ensure potential equalisation between the IO circuit and the field to prevent potential differences, but if I can't connect the equip bonding system to the protective earth how do I ensure personal protection??
I think what they are trying to do is prevent potential rise on the PE system (in the event of ground fault, etc.) from appearing on the Is system (specifically cable screens) and the problems this would cause if a second fault occured (i.e between Is circuit and cable screen)
Help??
Thanks
We have a Zone 1 IIA T3 (IEC) Hazardous area in which we are installing several intrinsically safe circuits
Were using Siemens ET200iSP which is an intrinsically safe IO rack system
Anyway, there's a line in the Siemens IO manual that says you're not allowed to connect the equipotential bonding system to the protective earthing conductor of the supply system.
It also says that the ET200isp rack and most of the Is equipment (including cable screens) needs to be connected to this equipotential earthing system.
I understand that they are trying to ensure potential equalisation between the IO circuit and the field to prevent potential differences, but if I can't connect the equip bonding system to the protective earth how do I ensure personal protection??
I think what they are trying to do is prevent potential rise on the PE system (in the event of ground fault, etc.) from appearing on the Is system (specifically cable screens) and the problems this would cause if a second fault occured (i.e between Is circuit and cable screen)
Help??
Thanks