Interpreting CSI SAFE results - PT Concrete 1

Status
Not open for further replies.

SoCal_Structural

Structural
Aug 12, 2017
11
Hello everyone,

I have run into multiple issues in designing Post-Tensioned Parking Structure, and hoping to get some feedback from you guys. A quick summary of the parking structure building:

- 8" PT SLAB (Slab is thicker than usual, Live load requirements (100 psf) for this building are higher than parking structures
- 14"x38" PT Beams spaced at 18' O.C.
- Some 24" wide PT girders
- 24"x24" Concrete columns

I have attached a pdf with snapshots of output from software as well as a quick hand check for prestressing force requirement.

Observations:

1) - Moments in beams are much smaller than anticipated - There is 35-40% difference between ETABS/Handcheck vs SAFE (SAFE MOMENTS SMALLER)

2)- All beams are failing - I am having to require insane amounts of Pre-stressing loads (and still failing) eventhough the moments are smaller than actual moments, this is going to get worse once I fix the moment issue.

3)- Flexure Reinforcing (non-prestressed) requirements are higher at mid span (for positive moments) than for end moments (negative), even though the end moments are larger.

Below are links to PDF results and SAFE model:


I tried messing the beam section properties in the model, by making it a T-beam and assigning it an effective width, but no effect on results. Tried without effective width (beam stem only) still no luck. Any feedback would be appreciated.

Thanks,
 
Replies continue below

Recommended for you

Responding to my OP since I initially posted this under a wrong category.

Thanks,
 
Kudos for recognizing that there is an error!

I do not use SAFE for PT design, but here is what I would do:

1. Forget about doing this as full 3D framing model until you have a grip on what is happening with SAFE on a 2D run.

2. Select a single grid line and model a frame: columns and beams over a single story.

3. Do some hald calcs of this single frame model and compare to SAFE’s output.

Based upon your loads and spans, you should be able to make this work with around 15 to 20 tendons, with balancing say 75% of DL. 30 to 50 tendons is not correct.

I would even suggest that you first model a simply supported 64’ span beam with pin supports (no columns) and check that output to your hand calcs. Then venture to a column/beam 2D model.

Start simple, understand what SAFE is doing, then maybe extend that to 3D if truly warranted.

Based upon 17 tendons, I get 360 psi of flexural tension at midspan under service conditions, about 5.5 in2 of bottom midspan rebar (for ultimate), and long-term deflection of less than 1”. This was modeled on 100% column fixity with an assumed column height of 10’ so there is a negative moment demand at ultimate requiring about 7 in2 of bonded rebar.

As you alluded to, for a 18' span slab with a 8" thickness (even with LL of 100 psf) that is pretty thick: L/D = 27, and results possibly in 'unnecessary' additional load to take up on the PT beams.
 
Thanks for the insight, Igenuity.

After playing with many variables, I decided to re-import my model from ETABS. However, this time for every small change made I ran the analysis, so I could narrow down when/if something went wrong.

My results are much better than the previous model. I noticed that the moments dropped in the beams after adding tendons in the beams, while the load case was dead only, I noticed that the program considers post tensioning regardless of the load case selected. Subsequently ran my model with 20 tendons (quick check), the beams appeared to all pass.

I hit my milestone for the evening, will be back at it in the morning. You are right, I thinking it will end up being somewhere between 17-20 tendons.

If I run into issues on this model, I will follow what you said and start with just a member design.

All said, I think the culprit may have been the column/support stiffnesses (i may have messed with the supports in my first model).

Thanks again!
 
Never used it, but you should be able to get individual load case values or total ultimate, unaffected by load balancing effects. They should be similar to Etabs.
 