Suggestion to kam-elec (Visitor) Jul 22, 2002 marked ///\\I must design and make an IPT for a 3 phase 12 pulse Rectifier(with two transformer Delta-star & Delta-Delta).
Which specifications must this IPT have?
///Essentially, this will depend on your downstream converter. Usually, phase shifters are designed for diode rectifiers. The controlled rectifier often form so-called Active Front End (AFE). Sometimes, it is possible to use off the shelf transformers. It depends what W, or kW or MW size of conversion you are dealing with.\\How is general method for designing an IPT?
///Usually, they are sized higher than the load, e.g. 1.4 times, to account for harmonics. There is a good more theoretical publication available from IEEE Press:
Paice D. A. "Power Electronic Converter Harmonics - Multiple Methods for Clean Power," IEEE Press, NY, 1996.
However, the more practical reference will be needed if detail calculations are required. See
Transformer and Inductor Design Handbook
by Colonel Wm. T. McLyman, Colonel William T. McLyman
Handbook of Transformer Design and Applications
by William M. Flanagan (Hardcover)
Handbook of Transformer Applications
by William M. Flanagan\\