Design criteria:
Internal and external are basically the
designer's choice, subject to local code.
Probably (very good idea) chosen from CIBSE /
ASHRAE / other guides.
unless specified in your local code, there is
no black and white requirement. However in some
countries there is a minimum temp. covered my
labour laws.
If I chose a particular internal condition
temp. say 24 deg C, and prep calcs, they are
based on a set of external conditions.
Effectively, I am promising the owner that the
internal temperature, will be *maintained* ONLY
when the external conditions are within my
described conditions.
If unexpected weather conditions drive the
external conditions beyond the design range,
the internal conditions will vary also.
variance, since automatic control systems can't
maintain a single point without excessive
hunting - the designer would specify a
control range say -+/-1 deg C.
A sensible designer would specify, in the
design brief, the "DESIGN conditions" at the
outset.
However, these are NOT 'cast iron' guarantee's
that the internal conditions will be maintained
under every possible circumstance.
If the designer specified 24 +/- 2 deg at the
outset, during specified external conditions,
and there is no other hidden local code
requirement, the designer has achieved the
intent.
One might try to argue, using "best practices",
etc. however legally the designer is probably
safe, depending on documentation
my 2 cents