timm33333
Electrical
- Apr 14, 2012
- 198
In load flow, we designate loads as continuous (100% demand) and intermittent (50% demand). So if we have four loads of 100kVA, one of them is continuous and other three are intermittent: then the general practice is to size the transformer for 100+50+50+50=250kVA.
Is this a correct practice to size the transformer? I think even if three loads are intermittent, still there is possibility that all four loads will be turned on together at some point, and at that point the total load will be 400 kVA; and so the 250 kVA transformer will not be enough. What do you guys think? Thanks
Is this a correct practice to size the transformer? I think even if three loads are intermittent, still there is possibility that all four loads will be turned on together at some point, and at that point the total load will be 400 kVA; and so the 250 kVA transformer will not be enough. What do you guys think? Thanks