IEEE Std. 242 2001 in page 314 describe how to obtain the overload curves (i.e. intermediate zone characteristics) for cables. this is the zone between the continues load capability and the short-circuit capability. It says:
"Intermediate zone characteristics of medium-voltage cables and 75 °C and 90 ˚C
thermoplastic cables are tabulated in Table 9-6 with the characteristics of medium-voltage
cable illustrated graphically in Figure 9-17a. These factors all apply to preloading at rated
ampacity at 40 ˚C ambient temperature. For lower ambient temperatures and when cable
ampacities have been increased to take this into account, the intermediate overload current
percent should be reduced by the following factors for each degree decrease in ambient
temperature below 40˚C"
I believe this might be wrong. The overload curve should be increase by that factor if the cable is operated at a ambient temperature below 40˚C. By increasing this the overload capability by that factor, the overload curve moves to the right (instead to the left) therefore you may overload the cable a little bit more at lower ambient temperatures.
Is my reasoning wrong? If it is, why?
Thanks.
Thanks.