odlanor
Electrical
- Jun 28, 2009
- 689
Our criteria for CT secondary cable shield grounding is:
- For power house: cable shield grounded at the one ends.
for outdoor substation: cable shield grounded at the two ends.
The route of the CT secondary cable is not straight from CT to relay. There are intermediate terminals.
The question is:
can we assume sections of shielded cable for grounding, or we must keep shielding continous?
We prefer sections like:
1-shielded cable from CT to junction-box1: Grounding at CT;
2-shielded cable from junction-box1 to junction-box2: grounding at junction-box1;
3-shielded cable from junction-box2 to relay board: grounding at junction-box2;