tajmeaw
Structural
- Mar 13, 2008
- 7
I am designing a multi-family residential wood framed building and am interested to see what other people are doing about a situation that I am having. I am using the tenant separation walls and corridor walls for shear walls. But on the interior of the unit, they are framing the non-load bearing walls before the gyp sheathing is put in place. By doing this I'm thinking they are creating several small shear walls instead of having one long shear wall. There seem to be several options.
1. Make them frame the intersection walls short of the shear wall so you can place the gypsum board behind the wall.
2. Analyze the wall as several smaller shear walls rather than one long shear wall.
3. Transfer the shear from one side of the intersecting wall to the other with nailing the studs together on either side of the wall.
4. Neglect this fact and design the wall as one long wall.
Thanks for the information
1. Make them frame the intersection walls short of the shear wall so you can place the gypsum board behind the wall.
2. Analyze the wall as several smaller shear walls rather than one long shear wall.
3. Transfer the shear from one side of the intersecting wall to the other with nailing the studs together on either side of the wall.
4. Neglect this fact and design the wall as one long wall.
Thanks for the information