Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

interconnection

Status
Not open for further replies.

Mlmlzx

Electrical
Joined
Feb 3, 2021
Messages
57
Location
NP
dear sirs,

i have to connect 132kv single circuit transmission line to 1200 amps generating substation in busbar.

what all are required?

Regards,
 
A professional engineering firm with experience in this work.
 
Typically, in India anyway: Dead end station tower, LAs, one to three CVTs, isolator, CT, SF6 breaker, two more isolators, and a structure to expand Bus I and Bus II if not already present. Zebra jumper cables and a dozen strain insulators. And of course ground grid, conduit, relaying, ect.

This is based on a general assumption of what may already in place, in reality your design may deviate from this.

 
why one to three CVT? one per phase?
could you please furnish sld?
 
One per phase- depending on where you pull your step distance and directional voltages (either the bus or line) you will need need 3 line CVTs for the prior, one for the latter. Only one CVT is needed for sync check.


Would these two diagram help?



It shows a wave trap in each bay, however with optical pilot ground wire that is becoming less common.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top