EngDM
- Aug 10, 2021
- 757
Hey all,
I'm hoping I can get some thoughts on how to interpret clause 13.10.6.1 of CSA A23.3. It has sum(Asb)=2*Vse/fy.
The symbols glossary out front of the code has Asb being "the minimum area of bottom reinforcement crossing one face of the periphery of a column and connecting the slab to the column or supported to provide structural integrity". So I interpret the sum(Asb) to be the summation of all four faces of my column.
Is this to say, that if I count each shear plane of each integrity bar to make up Asb? So in the image below, I have a total of 9-30M bars (3 vertically, and 6 horizontally). Would my Asb then be 9*2*700 = 12600mm^2, since each of the 9 bars has 2 shear planes?
Reason I am asking this is because in a textbook I have "Reinforced Concrete Design - A practical approach by Brzev and Pao" their design example calculates a required Asb of 1235mm^2, and then they go on to say they require 8-15M bars, which if taken as a single shear plane is 1600mm^2, but if taken as double shear plane as I've done in my example above, it would be 3200, in which case they would only need to have provided 4-15M bars (2 horizontal 2 vertical).