I have a motors maintenance manual withe following information regarding insulation testing of 3 phase motors:
Quote:
4.1.2 Measurement of insulation resistance
During and immediately after measuring, the terminals must not be touched as they
may carry residual dangerous voltages. Furthermore, if power cables are
connected, make sure that the power supplies are clearly disconnected and there
are no moving parts.
For rated voltage below 1000V, measured with a 500 VDC megger.
(b) For rated voltage above 1000V, measured with a 1000VDC megger.
(c) In accordance with IEEE 43, clause 9.3, the following formula should be applied:
R insulation ≃ Rated voltage ÷ ( 1000 + 1) x 10(MΩ)
(d) On a new winding, where the contaminant causing low insulation resistance is generally
moisture, drying the winding through the proper application of heat will normally increase
the insulation resistance to an acceptable level. The following are several accepted
methods for applying heat to the winding:
(1) If the motor is equipped with space heaters, they can be energized to heat the
winding.
(2) Direct current (as from a welder) can be passed through the winding. The total current
should not exceed approximately 50% of rated full load current. If the motor has only
three leads, two must be connected together to form one circuit through the winding.
In this case, one phase will carry the fully applied current and each of the others, one-half
each. If the motor has six leads (3 mains and 3 neutrals), the three phases should be
connected into one series circuit.