Hello ksps100
With all respect, some of us have been watching this scenario for decades. It is common for electronic people to not understand grounding systems. An instrument circuit may be connected to ground rods, but if it is not properly connected to the main system ground, lethal voltages may be developed between the instrument inputs and the structure supporting the instruments.
By the same token, the same voltages that may be lethal may be developed between the instrument grounds and the grounded circuit conductor.
The reason that neither the NEC nor the CEC give a minimum spacing for "Dedicated instrument grounds" is that it doesn't matter.
The codes state that all the grounds must be connected together.
ALL THE GROUNDS.
THAT'S THE LAW.
The inspector will not sign off the permit until the electrical contractor connects the two systems together with the connection mentioned by skogskura.
I have always understood that professionalism meant consulting with experts in any field in which you are not trained. For more than 40 years I have been astonished and embarrassed by the lack of understanding that many communications experts have of grounding principles, and even more by the indications that they don't know that they don't know.
I would also point out that in the event that the connection between the dedicated ground and the system ground is less than the code minimum ampacity for the system ground, (When the engineer says "It's only an instrument ground, it doesn't need to be that big.") a serious ground fault has the potential to destroy the undersized connection jumper and allow dangerous voltages to develop.
Any station engineer calculating voltage gradients can show you locations for a "Dedicated" ground rod cluster that will be guaranteed to result in dangerous voltages between ground systems in the event of a serious ground fault.
We have all seen many instrument ground systems, and the reason that there is not problems later is that the contractor has to make it safe before he leaves the site or the inspector will not allow the utility current to be connected.
I guess it's partly the fault of the power group, because we know that it's not worth talking to the instrument people when it's so quick any easy to inatall the appropriate jumper to make the system safe. I am sure that most comunication engineers never learn that the reason that they have excellent grounds is because the instrument ground has been connected to the much more extensive and effective main ground after they left the site.
If you consult the NEC for the minimum ampacity grounding conductor for the main grounding system and use that ampacity for the connection between the main grounding systen and the instrument ground bus, you will be safe and almost legal and your engineer will be happy.
end of rant