All,I have worked in several plants that have a hardwired Instrument-Air-Dump switch. In every case the plant was extremely uncomfortable with the thought of actually using this system as you might imagine. One of these plants was a large hydrocarbon processing plant with a full-fledged SIS system installed that required two switches to be simultaneously pulled on opposite sides of the control room in order to dump the air. Other plants had a simple covered quarter turn switch.
Is there a requirement that anyone knows of in any code or standard to have an instrument air dump? We are having difficulty thinking of a plausible scenario in which we would use such a system. This facility does not have an SIS. We only have a DCS and a few PLCs to control our facility.
For the SIS-system case I was under the impression that it existed for the highly unlikely scenario in which a nearby lightening strike / power surge only partially destroys the brains of the SIS, causing it to act in a "crazy" manner. Then the air would be dumped to stop the insane control system from creating unsafe situations in the plant. I know the likelihood of this scenario is vanishingly small, but this is what someone verbally suggested to me once.
The other scenario is that in the event things get so bad that the control room must be abandoned in some kind of a disaster, then the last thing that the last two operators would do before "abandoning ship" would be to trip the instrument air dump. This scenario is only slightly more likely in my opinion. Our control room is in an over-pressure resistant building.
Does anyone else have any experience with this sort of thing? Are there any regulations or ISA standards or SIS standards that address this?
Thanks,
JJJ