Hi Lionel.
The breaker had been replaced with a breaker "out of the box" with no attention at all to the settings.
The point is coordination.
Without proper coordination, an upstream breaker may clear a fault with much more serious consequences than a local trip.
This case was a tragedy of errors and incompetence.
1. A breaker was replaced by an electrician who didn't know that he should match the settings on the new breaker with the breaker being replaced.
2. A fan was removed from service and the leads were shorted together and to ground in a wire nut, for safety.
3. a lock-dog was installed on the 30 Amp breaker.
4. Another electrician, even dumber than the first, was playing with the 30 Amp breaker. (He will never work there again.)
5. Despite the lock-dog he managed to turn the breaker on.
6. The main breaker had the ground fault set at zero time. (The original breaker had a time delay set on ground fault trip.)
It was speculated that the breaker went out on ground fault faster than the 30 Amp breaker could trip on overload.
(The original breaker had a time delay set on ground fault trip.)
7. When the lights went out the electrician turned the breaker off and left the area.
8. With the breaker off and not tripped, there was no indication as to the origin of the fault. Eventually someone who had seen the idiot playing at the panel tipped off the trouble shooters.
9. The electrician eventually admitted what he had done, after a couple of millions of dollars of down time.
Again the point is that proper coordination will avoid a main breaker tripping when a branch circuit breaker should clear, and if fuses are required to achieve coordination, so be it.
The problems of a main breaker trip may be much more serious than the time to replace a fuse.
Bill
--------------------
"Why not the best?"
Jimmy Carter