Dear Mr. Mbrooke
Q. Are these "instantaneous elements" required to be enabled or present in molded case circuit breaker and power breakers?
A1. There are different terminologies, testing methods/Standards. In the States (UL, ANSI) and in Europe (IEC). UL uses the term "Power breaker", while IEC uses the term " Air circuit-breaker" etc....
A2. In Europe, IEC 60946-x prevail. Where a "Circuit-breaker is a mechanical switching device, capable of ( making, carrying and breaking currents under normal circuit conditions)* and also ( making, carrying for a specified time and breaking currents under specified abnormal circuit conditions)** such as those of short-circuit"
A3. All moulded-case circuit breaker fulfill the ( making, carrying .... under normal circuit conditions)* but having very limited capability to fulfill the (making carrying for a specified time and breaking current under specific abnormal circuit conditions )**, such as those of short-circuit".
This can be illustrated by a [current-limiting circuit-breaker] with a " break-time short enough to prevent the short-circuit current reaching its otherwise attainable peak value". A 100kA [current-limiting circuit-breaker] does NOT experience 100kA flowing through the contacts during testing! Therefore, "instantaneous elements" is required, as it has very limited capability to fulfill the (making carrying for a specified time and breaking current under specific abnormal circuit conditions )**. It has very low [rated short-time withstand current (Icw)].
A4. In Europe, an Air-circuit breaker is usually of sheet structure housing the circuit-breaker. Invariably, all ACB are tested to Icw to 1s or 3s with utilisation category B (Per IEC 60947-2).
An ACB rated Icw of 75kA 1s would be say 65kA 3s. The full value of the test current flowings through the contacts for the duration stated, during testing. An ACB may have the "instantaneous elements" switched off and the internal short-circuit protective device removed.
Che Kuan Yau (Singapore)