ndwade
Electrical
- Mar 26, 2009
- 14
Hello fellow engineers,
I work at a Chiller and Refrigeration Plant where we are experiencing Chiller Tripping issues without being able to find the root of the problem.
Our York chillers seem to 1st experience a "control power failure" during start up then once they reset the control power and go to start the Compressor Motor for the Chiller, it trips at the main gear. I've been told that this mostly happens to just one Compressor, but it has happened to others as well.
The gear trips off on Instantaneous to Ground w/ the following current values across each phase;
I(a) - 1,645A
I(b) - 1,589A
I(c) - 1,135A
I(G) - 1,211A
Here, we see that there is a high ground current and the Chiller trips on Instanteous to Ground with the extremely high current going to ground.
The avg operating current is about 200A for the chillers. The motor is 4160V, approx. 1600 - 1700 HP motor which runs @ 3500RPM. I've been told that the motors have never fully been taken down for maintenance in their 10yr history.
Because of the absence of burning or melting @ the starter, we are under the impression that there is a problem with the motor that is causing the high currents to go to ground.
As I am fairly new here, i'm relying on the word of the people that were here before me who say that the motor for the highly problematic compressor has been hypot-tested and megged out.(the method of the hypot-testing was questionable so i've been told)
In your opinion, what type of problems does this situation point to? Motor, motor starter, switchgear, Power quality?
Any input or help that you can give is much appreciated.
Thanks for you time and I look forward to hearing your views.
Respectfully,
Nadir
I work at a Chiller and Refrigeration Plant where we are experiencing Chiller Tripping issues without being able to find the root of the problem.
Our York chillers seem to 1st experience a "control power failure" during start up then once they reset the control power and go to start the Compressor Motor for the Chiller, it trips at the main gear. I've been told that this mostly happens to just one Compressor, but it has happened to others as well.
The gear trips off on Instantaneous to Ground w/ the following current values across each phase;
I(a) - 1,645A
I(b) - 1,589A
I(c) - 1,135A
I(G) - 1,211A
Here, we see that there is a high ground current and the Chiller trips on Instanteous to Ground with the extremely high current going to ground.
The avg operating current is about 200A for the chillers. The motor is 4160V, approx. 1600 - 1700 HP motor which runs @ 3500RPM. I've been told that the motors have never fully been taken down for maintenance in their 10yr history.
Because of the absence of burning or melting @ the starter, we are under the impression that there is a problem with the motor that is causing the high currents to go to ground.
As I am fairly new here, i'm relying on the word of the people that were here before me who say that the motor for the highly problematic compressor has been hypot-tested and megged out.(the method of the hypot-testing was questionable so i've been told)
In your opinion, what type of problems does this situation point to? Motor, motor starter, switchgear, Power quality?
Any input or help that you can give is much appreciated.
Thanks for you time and I look forward to hearing your views.
Respectfully,
Nadir