applebit42
Structural
- May 19, 2011
- 3
I am needing some opinions on the best way to install a reinforced concrete wall next to a footing.
In the interior slab of a building I have to install a 13'-6" deep pit that mechanical equipment will be installed in. The pit roughly needs to be 16'- 9" feet wide and will be centered between two interior columns. The column spacing is 20'-0" bays. This leaves me 10" to the edge of the base plate to the inside face of the wall for column line "A" and 1'-1" from the edge of base plate to inside face of wall for column line "B".
I want to install a 10" thick concrete wall that will be 13'-6" deep. We are going to put sheet pile down around the outside perimeter of the pit. The sheet piles will be left in place and are going to pour the outside face of the wall up against the sheet piles.
My question is that I am excavating so close to the footing. Would it be best to temporarily support the load of the column and then excavate down to the pit footing elevation (13'-6") and re-pour a pedestal under the temporarily supported footing (ie 12'-0 pedestal)?
The interior columns are all tied together with 2'-4" deep x 18" wide grade beams on four sides of the footing like a waffle. The soil type is clay sand with a bearing pressure of 4,000 psi. Maximum column load is around 45kips.
In the interior slab of a building I have to install a 13'-6" deep pit that mechanical equipment will be installed in. The pit roughly needs to be 16'- 9" feet wide and will be centered between two interior columns. The column spacing is 20'-0" bays. This leaves me 10" to the edge of the base plate to the inside face of the wall for column line "A" and 1'-1" from the edge of base plate to inside face of wall for column line "B".
I want to install a 10" thick concrete wall that will be 13'-6" deep. We are going to put sheet pile down around the outside perimeter of the pit. The sheet piles will be left in place and are going to pour the outside face of the wall up against the sheet piles.
My question is that I am excavating so close to the footing. Would it be best to temporarily support the load of the column and then excavate down to the pit footing elevation (13'-6") and re-pour a pedestal under the temporarily supported footing (ie 12'-0 pedestal)?
The interior columns are all tied together with 2'-4" deep x 18" wide grade beams on four sides of the footing like a waffle. The soil type is clay sand with a bearing pressure of 4,000 psi. Maximum column load is around 45kips.