Wiring a soft starter inside the delta provides NO BENEFIT other than being able to use a smaller (translate: cheaper) soft starter. It does however add significant risk of catastrophic failure unless additional hardware is added, which would of course negate the cost savings issue and increase the complexity, thus the number of things that could go wrong. It also increases the motor heating during starting and an incorrect connection can result in motor damage.
When a soft starter is wired normally (DOL as you refer to it), if one SCR shorts, there is no immediate risk of damage because there is no return path for current flow through the motor windings. You need at least 2 shorted SCRs in opposite phases to present a risk. In a soft starter wired inside the delta, if ANY one SCR shorts, you can lose the motor in short order because 1/2 of the current path through the windings is always present in that configuration. So the prudent course is to use what is referred to as a "fault contactor" in the circuit that opens up if there is any kind of fault on the circuit, i.e. shorted SCR, thus isolating the motor windings. Now the cost and space savings of using the soft starter rated for 58% of the motor FLC is offset by the cost and space required for the Fault Contactor and additional wiring.
There is also a theoretical need to use SCRs rated for a higher PIV rating when used inside the delta compared to a standard line connection because the potential peak voltage is higher. This is ignored by most soft starter manufacturers who promote this configuration because it would add cost, but technically using standard rated SCRs in starters wired inside the delta make them MORE prone to shorting. This argument has been ongoing in the industry, unbeknown to many smaller manufacturers who simply copy what other people do.
Harmonics during soft starting are generally considered insignificant, but when the soft starter is connected inside the delta, the non-sinusoidal nature of the current is exaggerated and THD is TWICE that of a standard connection. So for the same amount of starting torque, more of the current is being wasted as heat in the motor or conversely you get less torque-per-amp during start. So if your application requires a long start-up ramp or frequent starts, using an inside the delta configuration will result in more thermal stress in your motor.
The connection pattern of a standard line (delta) connection is somewhat simple, just get the rotation correct. On the other hand, connecting inside the delta is extremely specific, the pattern must be followed exactly, otherwise the motor windings can be damaged almost immediately upon energization. There is little room for error, yet almost nobody is familiar with exactly how to do it (other than following the written instructions explicitly). For the average end user, this can present a significant risk of future problems during an emergency repair.
Bottom line, inside the delta is not worth the risk IMHO.
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams