11Kv SYSTEM with only generator as power source, 2x2.2MW+3x4.375, the short circuit proctection setting for 2,2MW - I>1.2In, 10s, I>>2.5In; 4.375MW, I>1.2In, 5s, I>>1.5In, 0.5s.
We put one 10MVA transformer in, all of Genset shunt down due to inrush current of closing.
My question is how to set the correction setting; if the seeting is changed to standway from inrush current, the small genset could be damgaged or not.
We put one 10MVA transformer in, all of Genset shunt down due to inrush current of closing.
My question is how to set the correction setting; if the seeting is changed to standway from inrush current, the small genset could be damgaged or not.