Not meaning to beat a issue to death, but the bench set is the air pressure required to move the valve through its full stroke (ie, "open to close" or "closed to open", depending on whether the actuator is a reverse or direct acting actuator. The "bench set" values are based on the fluid system pressures that you provided the manufacturer (ie, Fisher) when you purchased the valve. By knowing your system conditions, the vendor then selects the correct actuator and spring to meet your system conditions and shut off requirements. Be careful not to confuse the bench set values with the spring range, which can also be stamped on the nameplate. The spring range is a nominal range of a spring (3-15, 5 - 12, etc) based on its spring rate and travel and is not a parameter to be utilized when setting up the valve. As one of the previous replys noted, the actautor is setup either on a bench or in the field, but always with the actuator stem disconnected from the valve stem. The the "lower bench setting" air pressure is applied to the actuator and until the actuator just begins to move (the spring tension adjuster is adjusted util travel begins at the lower bench set) Then the travel or stroke of the actuator is measured as pressure is increased util rated travel is attained (should almost exactly at the upper bench setting). After setting up the actuator, the assembly of the valve and actuator can be tested together in the field by using the Flowscanner, which measures things such as packing load, hysteresis, positioner signal etc. Best to call and talk with a Fisher Rep.