I worked on a large dragline a little less than 30 years ago. (75-80 Cu. Yd., 320 ft. working radius.)
Main hoist 8 x 1300 Hp., Drag 8 x 1050 Hp.
Each motor was direct connected to its own generator. The motors had constant field excitation.
The Generator field control was solid state. There may have been an exciter between the electronic controls and the generator fields, but I don't remember. 200% Field forcing was also used for fast response. That is, for example, if the operator moved his control to increase the speed from 40% to 50%, the output of the solid state module would go to 200%. When the circuits determined that the speed had reached the intended 50%, the output of the solid state module would drop to maintain that speed level.
If you are trying to follow the control logic, watch for field forcing circuits.
Another issue with draglines is lowering a loaded bucket. If the operator tried to lower a loaded bucket instead of dumping it, the load compensation would act in reverse and accelerate the downward travel. This would increase the current and the circuits would erroneously interpret this as an increased load and increase the field. Field forcing would cut in and the motors would go into runaway, while the loaded bucket free fell.
You may find other logic in the control circuits to avoid this issue.
But hey, isn't there anyone on the forum with more recent experience on draglines?
respectfully