Infiltration Trench
Sathre
15
Does anyone have a good way to model a sloped infiltration trench? I have a 5 ft wide trench, 3 feet deep with, 300ft long at about 1.5% slope. Do you just set up the model with multiple custom stage storage? Do you need to have some sort of outlet from each storage to the next?
How are you planning to model the trench? If you're using a pond, you could use custom storage, but an easy "trick" is to use the pipe storage option with a 5x3 box.
However, your slope of 1.5% over 300 feet means that the trench drops 4.5 feet over it's length. Since the drop is greater than the nominal 3 foot depth, you really only have 3 feet of available depth (at the low end) tapering to zero depth after 200 feet. The remaining 100 feet will never hold any water - assuming a level water surface.
Peter Smart
HydroCAD Software
Is the extended length intended to be a reserve?
Mike McCann, PE, SE (WA)
No, the extended length is to catch runoff. I am running the trench across the rear yards of 7 lots in a new development. I had modeled the trench as a pipe with void storage over the 3 ft depth (20%) and then an additional pipe storage above that of 1ft with 100% voids for live storage. So a small infiltration trench / ditch.