We had a bizarre case where noise in sensitive instrumentation (ion chamber detector) was highly correlated to operation of a particular 13.2kv motor. Specifically:
Immediately after starting the motor, the instrument noise began. So we manually monitored motor partial discharge on the motor (measured from coupling capacitor r/c filter output using Iris equipment), and found it was high (when it had never been before), but also a very unusual “pattern” (the pattern considers when in time the discharges occur in relation to power frequency voltage phase). We monitored partial discharge over a period of time and it went back to normal in the same timeframe that the instrumentation noise went away.
Several months went by. Instrumentation showed no problems, motor partial discharge measurements normal.
Then problem came back on instrumentation. We checked motor partial discharge and again high.
Correlation was undeniable. We were scratching our heads. How did the motor cause the instrument noise? We have suspicion the power cables for the motor pass near the detector cables.
Shortly thereafter while instrument noise was still present (and high motor partial discharge indicated), we also got intermittent undervoltage alarms associated with the motor (pt’s to feed this alarm are switched in when the motor is started).
Voltage measurements at PT secondary showed unusual/unbalanced results (measured using fluke... did not capture any waveform). So the PT drawer was opened for troubleshooting and fuses racked out. At that moment the instrumentation noise went away and the next check of motor partial discharge indicated normal.
Fuse was replaced but not saved. Fuse holders will be inspected at the next outage. No instrument noise or unusual motor partial discharge indiations since then.
I think we had an intermittent open circuit in the fuse or the fuseholder causing arcing. EMI from that arcing was coupled either along the power cable shielding to both the motor partial discharge detection circuit and to the unrelated ion chamber instrumentation circuit.
Although the source of the EMI was not at the motor in this case, I'm inclined to think it could be in other cases of medium voltage motors (it would not be a normal condition, but when there is a problem with a connection or with insulation).
=====================================