Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Induction Motor Equivalent Circuit Calculations

Status
Not open for further replies.

tiftif

Electrical
Joined
Jul 16, 2010
Messages
13
Location
CA
I have a motor info as
HP 500 , kVA 450, poles 2, kV 4.16, Slip 1.275 RPM 3554, SF 1.15 , FLA 65
PF FL 100% -> 86%
Eff 100% -> 95
Locked Rotor:
%LRC 690%
%PF 19, T = 35% Tmax = 210

Can you please help me with equivalent circuit calculation and provide me with some references to go from these parameters to equivalent circuit?
 
Induction_motor_500_hp_3600_rpm_schematic_znogyy.jpg

I can calculate the parameters using my software-hand made on VB6-but I cannot send the
calculation only the results.
I hope it may be useful in a way. It is not possible to be close more than 5% because we have to neglect some of the losses as ferromagnetic losses, friction and ventilation.
For instance rated current will be 63.34A instead of 65A, pf=0.904 instead of 0.86.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top