Inductance Calculation 1
Cerkit
100
I looking at calculating the inductance using the following equation
L = Voltage /( 2*pi*f*I)
Can I use the rms voltage and current for this calculation?
It doesn't matter. You have square root of 2 in the numerator for the voltage and a square root of two in the denominator for the current. They cancel out. You can use whatever as long as the ratio of voltage to current stays the same.
If you can't explain it to a six year old, you don't understand it yourself.
As HamburgerHelper said, rms is OK as long as both V & I are the same. Units do matter. If f is in Hertz, V is volts, and I is amperes, then L will be in Henries
Keep in mind that the equation is only correct if there is no resistance in the circuit.
I want to use it to get a rough feel of the magnitude of the Inductance for a transformer. If the magnetising current is 5A and the primary side voltage is 33kV.For a 50Hz system.
I get 21H for the inductance.
Right. But if you are looking for the transformer's inductance in the circuit, it is not what you need.
Gunnar Englund
Is it possible to get a value of inductance if I know the magnetising current?
Here are some common R% X% Z% values for transformers of different sizes. As you move up in size, X% makes up a larger portion of Z%. Enough so that for a rough ballpark number, you would not be off by much just to assume Z=X.
This doesn't matter unless you are doing high frequency transient analysis but there is capacitive coupling between the winding and the phases. The impedance of a transformer is a function of the frequency. High frequency transients can pass through the transformer through capacitive coupling without stepping up or down through winding couplings.