Lightecho has offered a superb example.
I would complete the NFPA 25 inspection components as usual. I would also have a clear and concise discussion with the customer/owner to inform him/her that the fire pump house alteration could potentially be a problem and that the specific issue or potential issues are not a direct violation outlined in NFPA 25; therefore, we will not list this potential problem as a deficiency. We are required to document this change/alteration on the NFPA 25 inspection form and we recommend a proper evaluation by the AHJ or a certfied consultant (i.e. FPE or qualified sprinkler contractor) to ensure/confirm in writing whether or not the change/alteration is acceptable or not based on all of the applicable NFPA standards and other pertinent state laws.
Excerpt from NFPA 25 (2002): "4.1.6 Where changes in the occupancy, hazard, water supply, storage commodity, storage arrangement, building modification, or other condition that affects the installation criteria of the system are identified, the owner or occupant shall promptly take steps, such as contacting a qualified contractor, consultant, or engineer, to evaluate the adequacy of the installed system in order to protect the building or hazard in question."
"5.4.3* Installation and Acceptance Testing. Where maintenance or repair requires the replacement of sprinkler system components affecting more than 20 sprinklers, those components shall be installed and tested in accordance with NFPA 13, Standard for the Installation of Sprinkler Systems."
This is the approach which I have instructed my employees to implement in these instances.............I wonder how other companies/inspectors would handle this situation. Please provide a response for the benefit of the blog participants if you have an opinion.
By the way.............the butterfly valves within 50 ft. of the suction side (rather than OS&Y valves) of the fire pump is not the only potential issue. I have found several instances where a BFP unit was installed after the fact which created either negative suction between the 100%-150% flow rates or reduced the available water supply so much that the "new" water supply was inadequate for some of the more demanding sprinkler systems at the facility. The fixed pressure loss and the residual friction loss associated with some BFP units can be very detrimental to fire protection systems!